    Grid imbalance moves to agent dispatch: MADWMPG holds cumulative violation cost at 0.006 on an IEEE 123-bus feeder

    For multiphase active distribution networks with phase-changing soft open points (PCSOPs, power-electronics devices that move active power directly between phases), MADWMPG hands three-phase voltage and feeder-head power imbalance dispatch to multi-agent safe reinforcement learning. A wide-margin classifier switches between behavior and recourse policies, and noncrossing quantile critics track the return distribution. On a modified IEEE 123-bus test feeder its cumulative risk-adjusted constraint violation score is 0.006, against 35.010 for DDPG, 4.571 for TD3PG, 5.103 for RCPO and 0.076 for PID-Lagrangian; average test step reward is 0.957, below the 0.989 of the ACOPF expert.